A typical 120-volt household circuit delivers 350 watts of power to an appliance, and another 10 watts of power are consumed by the circuit

Physics Oct 06, 2020

A typical 120-volt household circuit delivers 350 watts of power to an appliance, and another 10 watts of power are consumed by the circuit. There is no ground fault.

a. How much current is carried by the hot wire?
b. How much current is carried by the neutral?
c. How much current is carried by the grounding conductor?
d. Calculate the resistance of the circuit:

A certain string of Christmas tree lights has 100 bulbs, each rated at 500 milliwatts. The string of lights plugs into a standard 120 volt circuit. Assume that there is no ground fault. Calculate the current flow through the hot wire. Calculate the current flow through the neutral.

Expert Solution

As there is no ground fault, the same amount of current flows through the hot wire and the neutral wire.

a) Total power delivered to the appliance P = 350 W

Output voltage = 120 V

So the current drawn by the appliance, I = P/V = 350/120 = 2.92 Ampere -- Ans

Ground fault means some current is getting drained to ground. If that is the case, the current in Hot and neutral wires will not be equal.

In our case, both hot and neutral wire to the appliance carries

the same amount of current = 2.92 A -- Ans

Current through grounding conductor = 0 A -- Ans

The circuit consumes a power of 10W at 120 volt

Current consumed by the circuit I = P/V = 10/120 = 0.083 Ampere

Resistance of the circuit, R = V/I = 120/0.083 = 1445.8 Ohm -- Ans

Each bulb has a power rating of 500milli Watts on 120 V.

So the current required for one bulb is I = P/V = 0.5 Watts/120 Volt = 0.0042 A = 4.2mA

The total current drawn by 100 bulbs is then, I = 100 * 0.0042 = 0.42 Ampere

As there is no ground fault, the same amount of current flows through hot and neutral wire.

------------------------
Though the magnitude of current would be the same, they are opposite in direction. If you write a current I is flowing through the hot wire, you may say -I is flowing through the neutral wire. This is the principle behind the operation of Ground Fault Interrupters in your home.

As I and -I cancels, if you test for a magnetic field near a pair of hot and neutral wire, no net magnetic field will be there. If , for example, someone touches the hot wire, a ground leakage happens and the current through hot and neutral wires differs (hot wire has more current) and a net magnetic field is there. The sensing circuits detects this and switches off the Ground Fault Interrupter there by protecting the person.

Archived Solution
Unlocked Solution

You have full access to this solution. To save a copy with all formatting and attachments, use the button below.

Already a member? Sign In
Important Note: This solution is from our archive and has been purchased by others. Submitting it as-is may trigger plagiarism detection. Use it for reference only.

For ready-to-submit work, please order a fresh solution below.

Or get 100% fresh solution
Get Custom Quote
Secure Payment